The sequencing solution to the 180 A limit is the part of this worth copying, and the detail that makes it defensible is enforcing it in the control architecture rather than assuming it from the cycle. We did something similar on a two-cell resistance welding line and learned the hard way that a sequence which never coincides in the nominal cycle will coincide during recovery — an operator aborts, a weld is re-run, and suddenly two things that were never simultaneous are drawing peak together. Interlocking the peak-draw permissives so only one consumer can be in peak at a time makes the limit a hard constraint rather than a property of the happy path.
The other thing worth measuring rather than calculating is the actual peak draw, including the inrush on the positioner drive. Nameplate ratings and the sum of duty cycles will get you an estimate, but the current you have to design against is what a clamp meter and a data logger record over a full shift including faults and restarts. On our cell the measured peak was about 15 percent above the calculated figure, entirely from drive inrush during index, and on a supply capped as tightly as yours that margin decides whether the design works.